FAQs about EAp2 :

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

View answers »

Forum discussion

NC-2009 EAp2:Minimum Energy Performance

System 9 - Baseline

Greetings, The question is related to modeling rooms/zones which are to be assigned to System 9. In the Proposed, these rooms/zones are having supply, return and sometime room exhaust ventilation. When however a System 9 is to be modeled, the App. G mention the fan power related only to the supply air flow. What should be used for Return/Exhaust fan power for System 9. Your advice will be highly appreciated. Thanks

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 07/04/2017 - 16:54

The baseline fan power allowance includes all of the system fans. You can allocate the kW a number of different ways depending on the systems.

Wed, 07/05/2017 - 06:41

Hi Marcus, Thanks for the reply. The fan power for System 9 is clear - CFM x 0.3 - over. How about fan power adjustment for this system? In the Proposed there are filters and sound attenuators. How to add their static to the System 9's fan power. Without this the comparison is favorable for the Baseline and it shouldn't be so. Your opinion and advice are highly appreciated. Thanks.

Wed, 07/05/2017 - 16:30

There are no pressure drop adjustments for System 9 or 10. These systems only apply to certain space types such as storage rooms, stairwells, vestibules, electrical/mechanical rooms, and restrooms not exhausting or transferring air from mechanically cooled thermal zones in the proposed design. You cannot use these systems except for those space types. LEED allows them to apply to warehouses which I guess is just a large storage room.

Thu, 07/13/2017 - 09:35

Hi Marcus, Thanks for the reply. Practically, for system 9 what value for Static pressure is to be entered in the modeling software. Thanks.

Fri, 07/14/2017 - 16:36

Appendix G does not indicate a static pressure setting so it should be identical to the Proposed.