NC-2009 EAc1:Optimize Energy Performance

Theater lighting

I've gone through the threads and can't find a response for a question like this, there must be one, but we have a theater project with all of the speciality lighting associated with this use. It is an outdoor amphitheater, so the lighting use is very sporatic both programmatically and due to outdoor ambient lighting during daytime hours. The theater consultant wants to use incandescent lighting as much as possible for color, etc. Is this type of lighting included in the energy model. Is it excluded in anyway, or partially excluded due to patterns of use and scheduling?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 11/14/2014 - 16:34

All energy use associated with the project is always included in the models. There are no exceptions. Section 9.2.2.3 excludes theater lighting from the regulated requirements so you do not have to count it in the interior or exterior lighting power densities. It should be modeled as a separate process load identically in both models.