FAQs about EAp2 :

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

View answers »

Forum discussion

NC-2009 EAp2:Minimum Energy Performance

Unconditioned building envelope

Hi, I have a doubt on how to model unconditioned spaces envelope. As the baseline building meets the requirements of Section 5.5 (ASHRAE 90.1), the baseline building envelope would be modeled according to one of (or both) of the following: - If a building contains a conditioned space, the exterior envelope building envelope shall comply with either the "nonresidential" or "residential" requirements; - If a building contains any semiheated space or unconditioned space, then the semi-exterior envelope shall comply with the requirements for semi-heated space. My case wouldn't be the first one, since the building contains only unconditioned spaces. However, the requirements of the second option refers to semi-exterior building envelope, which does not refer to unconditioned spaces in contact with the exterior. How should I model then? Thanks.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 10/02/2013 - 15:16

If the entire building envelope is exposed to the outside (or the ground) and it is not conditioned at all then there are no insulation requirements. If a portion of the building is unconditioned and adjacent to conditioned space then the semi-heated envelope requirements apply.

Wed, 10/02/2013 - 18:18

Hi Marcus, In my case, all the building envelope is exposed to the exterior. So, if the insulation requirements do not apply, how should I model the baseline envelope? Which U values should I adopt? Thanks.

Wed, 10/02/2013 - 19:13

If it is fully unconditioned you will have some issues. See Table G3.1-10 Proposed (c) and (d). You are required to model a heating and cooling system identical to the Baseline system. This makes the space conditioned so you will therefore need to model the baseline envelope per the Table 5.5-X requirements. The proposed remains uninsulated I would assume for an unconditioned building. Potentially hard to show enough savings under this scenario to submit for LEED.

Thu, 10/03/2013 - 13:04

Hi Marcus, I read many discussions in this forum stating that "You do not have to model heating or cooling in unconditioned spaces", which would be my case. So, why should I model a heating and cooling system?

Mon, 10/07/2013 - 07:36

As I understand, if the space in the proposed design has either of mechanical heating or mechanical cooling, then you are required to model both, i.e. the missing mechanical system. Else, the space is unconditioned and requires neither.

Mon, 10/07/2013 - 13:41

There is an acceptable work around related to temperature set points that can render the requirement for a heating or cooling system a moot point. As a result adding such a system is often not enforced. In your case the level of insulation does not matter at all since the space is fully unconditioned. Insulation should have no effect on the results. Since this could go a couple of ways I would recommend that you check the LEED Interpretations for anything applicable and if you cannot find one to address your issue that you submit one.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.