Use of clerestories for IEQc8.1?

After review of the requirements for IEQc8.1, it appears to me that light from clerestories is not allowed in the calculations for this credit. Am I missing something?

1

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 02/24/2011 - 17:43

Karen, which path are you looking at? Clerestories should contribute to Options 1, 3, and 4, although I'm not sure about Option 2.

Thu, 02/24/2011 - 17:50

They do for Options 1, 3, and 4 as Tristan said. And they do for Option 2 if they are the only type of fenestration in the area and they are not obstructed by the ceiling. Option 2 was meant as a simple (read: cheaper) way to qualify VERY simple geometry.

Thu, 02/24/2011 - 19:40

Tristan, we were going for option 2. However, looks like we should pursue option 1 so we can include the clerestory. Jill, do you recommend a simulation software?

Thu, 02/24/2011 - 21:52

I can recommend a consultant. ;) If you have never used daylighting simulation software before, you will want to consider what it is worth to you to buy and learn the software vs. hiring a consultant. Find a consultant that has at least 3 years of experience with the software, knows what to expect from it, knows how to debug the results and can model complicated geometry without breaking the project fee. It is not plug-and-play technology.

Thu, 02/24/2011 - 22:15

Jill -- Ever used 3ds max software to model daylight? We know it is capable, just not sure it will give us exactly what we need to know for LEED. Thanks.

Thu, 02/24/2011 - 22:36

Sorry, I have not. Again, I would suggest weighing what it is worth to buy and learn the software vs. hiring a consultant.

Fri, 02/25/2011 - 03:16

I agree with you, Jill. To run a daylight simulation is not difficult but to run correctly, it takes time to learn. Understanding the physic of light and daylight is also required. Otherwise, it will be garbage in and garbage out.