Has anyone ever used the alternative compliance option for this prerequisite by following Appendix A of ASHRAE 62.1-2007? The equipment designed for our facility is a VAV (variable air volume) system supplying multiple zones.

3

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 05/17/2011 - 19:38

I have the same question. The build in calculator does not seem to support the Appendix A calculations. I see no other way to approach this other than to use the alternative compliance path, and upload the calculations. I'm also including a narrative explaining why we used Appendix A (multiple zone VAV system with some fan powered boxes). Hope that is enough! We won't be submitting for a while, so I would love to know anyone's feedback from USGBC if they have tried this approach.

Thu, 05/26/2011 - 13:27

Barbara, we have used this approach also. We've found that the letter template works better for smaller buildings and simple systems. As long as your spreadsheet is the ASHRAE provided one or a custom one that clearly outlines the Appendix A procedure and equations, you should be fine.

Thu, 05/26/2011 - 19:31

if using non-default occupancies for the LEED Online form (NC 2009) can actual occupancies be used, or must they be in terms of occupants per 1000 sf densities? For example, a 500sf office space with 1 occupant, can we use the value of 1, or must it be 2, since that is the occupant density per 1000sf? Thanks.

Thu, 05/26/2011 - 19:36

62MZ calculator seems to say 'actual occupancy' value is OK, but the LEED template column header indicates #/1000, so I think there is a discrepancy? 62MZ calc states "The design population of the zone. This will default to the number of people calculated using the default occupant density in Table 6-1. It may be overridden to the actual number of people expected to occupy the zone, which in turn may be reduced using time averaging where applicable."