FAQs about EAp2 :

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

View answers »

Forum discussion

NC-2009 EAp2:Minimum Energy Performance

Water-cooled screw chiller- Minimum Efficiency

Hi, I would like to seek expert advice in the following. 1) Can anybody advise if water-cooled screw chillers intended to operate at non-standard conditions (Middle East) must comply with Table 6.8.1C efficiency requirements? In ASHRAE 90.1 2007 Section 6.4.1.2, I could see only references to water cooled centrifugal chillers. 2) In LEED 2009, it is mentioned that we should follow ASHRAE 90.1-2007 without addenda for EAp2. And ASHARE has released an addendum in 2008 which contains major changes in equipment efficiency requirements. My question is, can I use this addendum for LEED NC 2009 project and if used, should I comply with all the addedum references in all sections.? If I want to use the addendum equipment efficiencies, should I also comply with all other sections in addendum.? many thanks in advance..

2

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 02/22/2012 - 14:21

1) The applied conditions do not matter. The efficiency is at the rated conditions. Equipment efficiency is a mandatory provision. This issue has been raised numerous times related to international projects. If equipment meeting the minimum efficiency is not available then explain the situation for the LEED reviewer but understand this is a risky thing to do for LEED projects as this could mean the project cannot earn the prerequisite. 2) There is a footnote which indicates that addenda may be used at the discretion of the project team. You must apply the addenda in its entirety and if applicable across any other LEED credits. You do not have to use them all if using just one.

Thu, 02/23/2012 - 07:45

Marcus, thanks for your advice. Could you please elaborate your statement 'You do not have to use them all if using just one'. Do you mean to say that I can follow the addenda equipment efficinecy requirements but doesn't need to comply with other addenda sections..?

Thu, 02/23/2012 - 22:30

There are several addenda. You do not have to apply them all, you can pick and choose. If you do apply one then you must use it in its entirety. You can't just pick out a part of an addendum.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.