FAQs about EAp2 :

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

View answers »

Forum discussion

CS-2009 EAp2:Minimum Energy Performance

WWR calculation - green wall - lattice

Hi all! I’m modeling a 49-story building with 7 basements, and it has over 40 % (about 85 %) of its envelope covered with glazing, so I have a doubt about the calculation on the Window to Wall Ratio, to work it out, I found the example G-D in the 90.1 User’s Manual ANSI/ASHRAE/IESNA Standard 90.1-2007 (page G-16). Something I was wondering about is how to exactly compute the WWR, specifically, I want to know if I should consider only the gross above-grade wall area (as the Ashrae Standard mentions, Table G3.1.5.c) or I should consider the gross exterior wall area including the above-grade walls and below-grade wall area as well (90.1 User’s Manual ANSI/ASHRAE/IESNA Standard 90.1-2007, page 5-47). This is necessary because I have to reduce the percentage of glazing for my baseline design, and I don't really know if I should consider the 7 basements to calculate that reduction. Last, my model also has a large green wall on a side and lattice covering almost all the building (with irregular shapes), so I would like you to share with me some information about how to model them please, because I haven’t seen anything in the Ashrae Standard about lattice and green wall. I think I only should consider the green wall in my proposed design, actually I was thinking about modeling it as a wall but changing the U-factor and R-factor, and with the lattice I had in mind something similar but modifying the U-factor and SHGC, but surfing on forums I found that it’s even more difficult to do it. I hope you can help me! Thanks in advance.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 08/16/2012 - 00:20

The WWR is calculated on the above grade walls/windows and would not include the basements. There does appear to be a potential conflict between the Standard and the User's Manual. The Standard applies if the User's Manual conflicts. The Appendix G portion of the User's Manual and the Standard seem to be in sync. I would treat the green wall areas as exterior shading devices assuming the lattice is added outside the wall/windows and the plants grow on the lattice. These can be modeled in the proposed but do not get modeled in the baseline. This would affect the solar loads but not the conductive loads so the U-value would remain that of the windows but the SHGC would vary. Depending on the planting material and climate the shading effect could vary seasonally. Be sure to include a thorough narrative explaining your modeling assumptions and you might even consider doing this as an exceptional calculation since this is not really a direct input in any modeling software I am aware of and so the saving claimed are called out. Good luck with this one.

Tue, 01/08/2013 - 12:05

Hi, The WWR is calculated based on gross-above grade wall areas, which includes the wall areas of conditioned and unconditioned spaces, right? If in my project I have, for example, 7 above-grade floors of parking area, which have no glazing area, should I consider the area of these 7 floors in order to calculate the WWR?

Tue, 01/08/2013 - 17:30

I do not think that uncondtioned wall area counts for this ratio.

Tue, 01/08/2013 - 19:22

But the gross above-grade wall area accounts for all the above-grade wall area, doesn't it?

Tue, 01/08/2013 - 20:42

No, not really. The walls of the unconditioned spaces do not need to be insulated or meet any of the other window performance criteria so they would not count toward the fenestration area requirements either.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.